Geofabrics pullout capacity & care to take while Tensile Strength of Geofabric ≠ Pull-Out Resistance
I am discussing a Landfill site with Geofab as a part of capping liner system where overlaying soil depth is limited and require slope stability assessment and to check any contribution from Geofab for FOS ?!?!?
1️⃣ Tensile Strength of Geofabric ≠ Pull-Out Resistance
If the geofabric has:
- Ultimate tensile strength = 21 kN/m
This value is already per metre width.
So whether the roll is 6 m or 8 m wide doesn’t change the design strength per metre strip.
For a 6 m roll:
- Total ultimate capacity across full width = 6 × 21 = 126 kN
But in slope stability or anchorage calculations, we always work per metre width, so:
Design tensile capacity = 21 kN/m (before reduction factors)
Pull-out failure occurs when interface resistance + anchorage resistance is less than the tensile force mobilised in the geofabric.
2️⃣ What Resists Pull-Out?Pull-out resistance comes from:
✔ 1. Friction + Adhesion (Interface Shear Resistance)
Between:
- Geofabric
- Underlying soil
- Overlying soil
✔ 2. Normal Stress from Overburden
σv=γ×H
For example:
- γ = 18 kN/m³
- H = 0.3 m
σv=18×0.3=5.4 kPa
3️⃣ Interface Shear Resistance
For Example:
- Cohesion (c) = 5 kPa
- δ = 11°
Shear resistance per interface:
τ=c+σvtanδ
=5+(5.4×tan11∘)
tan11∘≈0.194
τ=5+(5.4×0.194)
=5+1.05
= 6.05 kPa
Since you have top and bottom interface, multiply by 2:
2×6.05=12.1 kPa
This means:
Pull-out resistance from soil friction = 12 kN per metre length of embedment
Because:
kPa × 1 m width = kN/m
So yes — 12 kN/m of embedment length.
4️⃣ Anchor Trench Contribution
If a 700 × 700 trench gives about: ≈ 8 kN/m resistance
Then total pull-out resistance per metre strip:
12+8=20 kN/m12 + 8 = 20 \text{ kN/m}12+8=20 kN/m
and this is already very close to the 21 kN/m tensile capacity of the geofabric.
That means:
⚠ You are at the limit.
After applying reduction factors (creep, installation damage, durability), allowable tensile strength will be much lower — maybe 10–14 kN/m.
So in reality:
5️⃣ Why “100 kN/m Pull-Out” on YouTube is MisleadingPull-out capacity may control before tensile rupture.
People often confuse:
- Ultimate tensile strength of heavy geogrids (not geofabrics)
- Long embedment lengths (3–6 m)
- High overburden (2–5 m soil cover)
- Granular backfill with φ = 35–40°
For example:
If:
- H = 3 m
- γ = 20 kN/m³
- φ = 35°
- δ ≈ 30°
- C=0
σv=60 kPa
τ=60tan30∘≈35kPa
With 3 m embedment:
2×35×3=210kN/m
Now you see where big numbers come from.
But for:
- 0.3 m cover
- φ = 11°
- Low cohesion
There is no way you reach 100 kN/m.
6️⃣ Important Point You Mentioned (Very Good Observation)If soil is:
- Dry
- Non-cohesive
- Loose sand
Then:
c≈0
So resistance becomes:
τ=σvtanδ
With your values:
=5.4×0.194=1.05kPa= 5.4 \times 0.194= 1.05 kPa=5.4×0.194=1.05kPa
Double interface:
≈2.1kPa≈ 2.1 kPa≈2.1kPa
That is extremely small.
So yes:
In dry sandy soils with small cover thickness, pull-out resistance is very limited.
Anchor trench becomes critical.
7️⃣ Key Engineering TakeawayFor example:
✔ 300 mm cover
✔ γ = 18 kN/m³
✔ δ = 11°
✔ c = 5 kPa
Pull-out capacity ≈ 20 kN/m
Which is consistent and realistic.
The “100 kN/m” values only apply to:
- Deep embedment
- High normal stress
- High friction angle
- Geogrids in reinforced soil walls
Not for shallow geofabric anchorage.
So please be careful in selecting pull-out resistance of Geofabrics (Textile)